Impedance is the current limiting characteristic of a transformer and is expressed in percentage. This percentage represents the amount of normal rated primary voltage which must be applied to the transformer to produce full rated load current when the secondary winding is short circuited.
What should be the impedance value of a distribution transformer?
It’s a tested value that the manufacturers do for power distribution transformers and is used in the fault current calculation….Typical Percent Impedance Values.
Transformer Size (kVA) | Typical \%Z Values |
---|---|
2501-5000 | 6.5\% |
5001-7500 | 7.5\% |
7501-10000 | 8.5\% |
Above 10kVA | 9.5\% |
What is the formula for impedance in transformer?
Since impedance is defined as the ratio of voltage divided by current, using the known voltage and the derived current, the impedance looking through the transformer to the load can be found. 55.4 Zeq = I1 Equation 6: Notice that this lossless transformer was assumed to have no impedance.
What is the impedance voltage in transformer?
The \% impedance is formally referred to as impedance voltage. It is the supply voltage, expressed as a \% of rated voltage, that is required to circulate rated current through the transformer. It is measured in the factory by a short circuit test at rated frequency.
What is Z impedance in transformer?
The percent impedance (\%Z) is the percent of the rated load impedance possessed by a transformer. The percent impedance is important in that it allows us to: Calculate available fault currents (both individual and bank).
How do you measure impedance of a transformer?
For this, low voltage side of the transformer is short circuited, an auto transformer and voltmeter is connected to higher voltage side. An ammeter is connected to the lower voltage side(short circuited side). Initially the auto transformer is gives ZERO voltage. Now voltage is increased gradually.
How do you calculate the kVA rating of A 3-phase transformer?
So if you’re working with a three-phase transformer, instead of multiplying the voltage by the amperage and dividing by 1,000 to get the kVA, you’ll multiply the voltage by the amperage by 1.732 and still divide by 1,000 to get the kVA.