What size ground wire do I need for a 75 kva transformer?

What size ground wire do I need for a 75 kva transformer?

For example, a 75-kVA transformer with a 480-volt primary and 208/120 volt, three-phase, four-wire secondary would have a maximum primary current of 90 amps and a maximum secondary current of 208 amps. The secondary conductors would be required to be 4/0 copper using 75 degrees Celsius insulated (or better) conductors.

What size breaker Do I need to feed a 75 kva transformer?

The rated current of the transformer can be used as the basis for a breaker. The rated current of a 3 phase, 75 kva transformer is 112 Amps, which is 25\% of the rated current of a 125 Amp breaker.

How many amps does a 75 kva transformer draw?

Three Phase Transformers, Full Load Amperes (FLC)
KVA 208V 600V
75 208 72
112.5 312 108
150 416 144
READ ALSO:   Can bowel issues cause lower right back pain?

What size wire do I need for a transformer?

For Transformer, we should choose two types of cable such as the primary side and secondary side. The rating of the cable should be 150\% of the full load current. i.e if your transformer’s primary current is 450 Amps means, you should choose 450 *150\% = 675 Amps capacity size cable.

What is the weight of a 75 kVA transformer?

510 pounds
Technical Details

Manufacturer ‎Larson Electronics LLC
Part Number ‎MT-ATX-3P-480D-75KVA-208Y120-N3R
Item Weight ‎510 pounds
Product Dimensions ‎30 x 40 x 30 inches
Item Package Quantity ‎1

What is the weight of a 75 KVA transformer?

What type of wire is used for transformer?

Applications. Magnet wire is used in windings of electric motors, transformers, inductors, generators, headphones, loudspeaker coils, hard drive head positioners, electromagnets, and other devices.